The precast steps and the foundation probably move at different rates, so the joint between them must be flexible. I suggest excavating to the bottom of the steps unit, and back maybe 18 inches in each direction. Don't bother to ptach the joint between them with cement...it will only crack and open up again. Instead, apply about 18 inches of foundation dampproofing heavily to both the foundation and the steps unit, and then embed a heavy sheet of neoprene flashing into each side. The neooprene will flex and allow relative movement between the two, and should stop your water entry. You can probably get a roll of neoprene flashing at a roofing supply house.
Architect (NY) and Home Designer (PA)
|
| |
| Posts: 2382 | Location: Tobyhanna, PA | Registered: 24 October 2005 |    |
|
|
|
The flashing is not self-adhesive, but it will stick in the dampproofing coating. There is no need for an outer coat of dampproofing. You can backfill right away, but it might be a good idea to backfill with pea gravel.