I have 2 bedrooms on the 2nd floor of my Cape. They have crawl spaces in the front & back of the rooms. There is vented drip edge all around the house. There is gable vents & ridge vent installed.

Here is the problem. The 2 rooms are so hot, 2 air conditioners are not making a dent in keeping them cool. Its so bad that the hot air is coming through the recessed lights in 1 of my sons rooms. The ceiling is scorching hot too. I installed 2 plastic vents on both sides of the crawl spaces to try to let the air escape & it aint doing the trick. I am thinking about spray foaming right above the drip edge vent to keep the air from coming in. I am at wits end on this matter. Anyone have some guidance to putting an end to this??

Thanks

John
 
Posts: 2 | Registered: 09 June 2008Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
Did you check the spots where the crawl space walls meet the roof, to see whether there is a continuous unobstructed ventilation path, in each and every rafter bay, of at least 1 1/2 inches extending to the area above the room ceilings?

Did you check the installation of the ridge vents to ensure that the roof sheathing was cut away enough to allow hot air to exhaust? Is the ridge vent a metal external baffle type, or is it one of the worthless rolled ridge vents? The external baffle of a proper ridge vent creates a low-pressure area at the vent which helps exhaust hot air from the attic space.

Did you check the insulation values in the crawl space wall, and in the ceiling above the rooms?

Did you check where the crawl space floor insulation extends to the eaves to be sure that the insulation hasn't blocked the ventilation path, and that there is at least a 1 1/2 inch space above the insulation and into the crawl space?

It is neither rocket science nor wizardry. The questions I have asked reflect the fundamentals of roof ventilation, and the answer to your problem will be revealed by the answers to those questions.


Architect (NY) and Home Designer (PA)
 
Posts: 2439 | Location: Tobyhanna, PA | Registered: 24 October 2005Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
quote:
Originally posted by Richard Hetzel:
Did you check the spots where the crawl space walls meet the roof, to see whether there is a continuous unobstructed ventilation path, in each and every rafter bay, of at least 1 1/2 inches extending to the area above the room ceilings?

Did you check the installation of the ridge vents to ensure that the roof sheathing was cut away enough to allow hot air to exhaust? Is the ridge vent a metal external baffle type, or is it one of the worthless rolled ridge vents? The external baffle of a proper ridge vent creates a low-pressure area at the vent which helps exhaust hot air from the attic space.

Did you check the insulation values in the crawl space wall, and in the ceiling above the rooms?

Did you check where the crawl space floor insulation extends to the eaves to be sure that the insulation hasn't blocked the ventilation path, and that there is at least a 1 1/2 inch space above the insulation and into the crawl space?

It is neither rocket science nor wizardry. The questions I have asked reflect the fundamentals of roof ventilation, and the answer to your problem will be revealed by the answers to those questions.


or is it one of the worthless rolled ridge vents?

I cannot look from underneath to see if its been cut right but i went on the roof and it seems that the ridge vent is matted down to the point of just trapping everything underneath. I am going to rip off the vent & check to see if enough of the sheathing was cut back. If not, I'll do it right with a better vent system.
 
Posts: 2 | Registered: 09 June 2008Reply With QuoteEdit or Delete MessageReport This Post
Posted Hide Post
You may have found the problem. Good luck!

Oh, I should mention that the "net free area" of the ridge vent should be about the same as the "net free area" of the soffit vents. If you know the soffit you installed, you can look up the free area on the manufacturer's web site. It may give you a number such as so many square inches of vent area per square foot. Whatever that number is, that should be approximately how many square inches per foot of vent in the ridge vent, times 2 if it's venting both sides of the roof.


Architect (NY) and Home Designer (PA)
 